Can you turn off forced DVCC on a lynx smart bms

I have a new lynx smart bms 1000 on an installation with a Phoenix inverter from 2017. It's giving error 48.


We do not want DVCC anyway.


Suggestions?

DVCC
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
bartrs avatar image
bartrs answered ·

DVCC can't be switched off.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@Scott

It will be because the Phoenix can't be controlled by the DVCC.

You can ignore it, but I guess it is annoying.

The only way is to roll back to before the DVCC force on firmware. V2.33 I think.

But obviously that means you loose the features that have been added since then.

So really it is up to you what you want to put up with.