Output is not understandable. Recommends unnecessarily large controllers and doesn’t show its working to diagnose what is wrong with it.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Output is not understandable. Recommends unnecessarily large controllers and doesn’t show its working to diagnose what is wrong with it.
Perhaps share your array and battery details, and some one can help.
I'm having difficulties with it too. It seemed to be working a few weeks ago?
I've entered data for a very simple 6 panel (3 in series, two strings setup) of 445W aiko panels. The calculator wants me to buy a 150/85 for this! The short circuit current is just 13.6 amps. I certainly don't need the 85 amps the suggested model allows for: my max amps should be under 28! The 150/35 should be perfect.
I've read a few complaints about the calculator being weird: should I give up on it, or is this something I'm doing wrong?
@Malk @24V system voltage it looks correct , TCVOC (Australia)
Bear in mind that the 85A spec of the MPPT is on the battery side, not on the PV side. Your panels will produce a max power of 6 x 445 = 2670w and so, assuming 100% efficiency for a moment, that needs 222.5A at 12V or 111.25A at 24V or 55.625A at 48V.
Can you please share some more details?
You can also share your configuration of the calculator.
Additional resources still need to be added for this topic