question

scott-n avatar image
scott-n asked

BMV 700 install Help, Tech not figuring it out !

BMV 700 w/ blue tooth dongle installed into a 5th Wheel RV with 4 Wet cell 6V golf cart batteries wired series/parallel to a 2500w inverter/charger. When the inverter is turned off, the RV runs off the DC battery bank, when I need AC power the inverter is turned on and AC is throughout the entire RV. His first attempt resulted in moniter reading discharge from batteries only ( inverter off ) and no absorbson readings from shore power or when the inverter was on no discharge readings, second attempt resulted in discharge readings from inverter only, but when inverter was off no readings from the battery bank. Tech is now saying I possibly need another shunt ? The desired outcome is for the moniter to read my battery status from the 4 battery bank charging and discharging when using the batteries alone or when using the inverter is on. I dry camp alot and when I switch on the inverter to watch TV or wife uses a AC kitchen appliance the moniter keeps an accurate account of the battery status. When plugged into shore power or the generator the moniter can read absorption recharging the batteries and account for the difference.

The inverter is a brand new Xantrez Freedom 458 modified sine 2500w inverter/charger with automatic 30 amp transfer.

Little worried that the tech is going to damage my electricial system just changing things and hoping it will work? Any help is appreciated. I have searched for a wiring diagram for the 700 using 4 batteries and an inverter with no success.


Thanks

BMV Battery Monitorinstallationinverter current draw
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
JohnC avatar image
JohnC answered ·

Hi Scott. It sounds like your shunt is wired incorrectly.

https://www.victronenergy.com/upload/documents/Quickinstallsheet_BMV70x_part1_2.pdf

Note it's a battery monitor, and not designed specifically for separating loads or sources. Wired to the -ve side of your batteries, and could be considered the actual batt pole, with no wires bypassing it. Bypassed wires don't get measured.

If this isn't clear or applicable, perhaps post some pics of the shunt or a wiring layout.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

scott-n avatar image scott-n commented ·

Thanks JohnC for responding, I'm not doing the install personally, The RV tech is having problems and I just wanted to make sure that BMV 700 can be connected to monitor my 4 batteries....discharge and absorption rates ...using an inverter/charger. Last spoke to them yesterday and they were thinking I needed another Shunt. Is there a wiring diagram somewhere that will show the correct connections when using an inverter?

0 Likes 0 ·
JohnC avatar image JohnC ♦ scott-n commented ·

This might cover you. Don't be confused by the 'little' wires that are just sensors/comms. But it does show you where they go.

0 Likes 0 ·
1564295986784.png (837.9 KiB)
Show more comments

Related Resources

Victron BMV battery monitors product page

Additional resources still need to be added for this topic