We have an installation with 4 VE Direct MPPTs and an Octo GX. 3 of the 4 MPPTs are in a constant off state as shown in the photo. Second photo shows that they have an appropriate PV voltage and the battery SOC is only 30%.

We have tried switching the VE direct cables and also different VE direct ports on the Octo but it is always the same 3 units in the off state. The firmware was updated on all units and there is no error state on any of them.


Any ideas?



MPPT ControllersVE.Directgx device
mppt.png (53.5 KiB)
mppt-2.png (40.7 KiB)
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

scott-simpson avatar image scott-simpson commented ·

I am the engineer who was on site when this problem occurred. On the remote console connection, under the device parameters for each of the MPPT’s the connection states USB. This should be VE Direct. I believe that the MPPT,s are on the USB Bus not the VE Direct Bus. Anyone have any ideas how to rectify this?

0 Likes 0 ·
scott-simpson avatar image scott-simpson commented ·

Here is a screenshot of one of the MPPT's

0 Likes 0 ·
mppt-usb.jpg (43.7 KiB)
Show more comments
2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Stevo07
Engineer logged on to the Octo, the mppt's state the 'remote input' is not ok, can it be the remote bridge connection is missing?


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

@Stevo07 & @Daniël Boekel (Victron Energy Staff)

Apologies, there was some site glitch and some of your follow up comments were lost. This is as best as I could recover. I have reported the bug.


@Stevo07 : This fixed the issue, many thanks! It was not immediately obvious that this should be checked, do you know where this info is contained?


@Daniël Boekel (Victron Energy Staff) : It is in the start up procedure in the MPPT manual, under cable connection sequence. It also comes connected from the factory, so someone has removed it.

0 Likes 0 ·
wkirby avatar image
wkirby answered ·

Is the charger enabled in Victronconnect?
A disabled charger will show an "Off" state in Venus.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

scott-simpson avatar image scott-simpson commented ·

All the chargers are enabled in victron connect.

0 Likes 0 ·

Related Resources

MPPT Product Page

MPPT Error codes

MPPT 150/60 up to 250/70 Manual

VE.Direct protocol FAQ

Additional resources still need to be added for this topic