question

wolle4000 avatar image
wolle4000 asked

Charging on Victron Blue Solar MPPT 150/70 in dependence of SoC

SoC Charger MPPT Blue Solar

MPPT ControllersCCGX Color ControlSOCVE.Direct
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wolle4000 avatar image wolle4000 commented ·

I want to stop charging if Soc is e.g. at 80% and restart charging im Soc is less than 40%.

I have a Blue Solar MPPT 150/70 Ve.Direct, connected to my CCGX.

With the quattro I already get a solution (via GEN Set Start / Stop )

Where can I set this parameter ?


0 Likes 0 ·
1 Answer
Paul B avatar image
Paul B answered ·

Presuming that you also have a bmv-7?? installed and connected

In the CCGX unit under settings change the relay to Generator start/stop

then under settings select the generator start/stop option and under conditions using SOC you can control the CCGX relay state, then use this relay to turn the Solar Charger off at 80% and back on at 40%,


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wolle4000 avatar image wolle4000 commented ·

How can I turn the MPPT on/off via the relay from my CCGX?


0 Likes 0 ·