Technical explanation requested on true Power Assist vs (D)ESS power assist like capabilities

We have been installing quite some systems supporting ESS and (D) ESS.
The installation of these systems require lots of reading and proper designwork according to Victron manuals and trainings.

Lately I have come a cross collegue's in the Victron World but also websites selling or telling the story that true PowerAssist is part of the ESS Assistant and ESS Venus OS functionality.
I have also read almost "all material" there is to read and although I have seen "PowerAssist like" behavior in ESS systems, I need to know the technical/design difference.
ESS Documentation is truly telling that the PowerAssist (boost factor) setting is being ignored when enabling ESS.

ESS design and installation manual (victronenergy.com)
Page 8 : The PowerAssist setting in VEConfigure3 will be disabled and ignored when ESS is installed.

Is somebody from Victron Staff, able to explain this ?

Below some questions that I have in general that require the explanation from Victron.
F.i.: What is the technical difference or equality or is the setting ignored but the function is still there ?
Which settings does it then use if so ?
F.i If there are PA like behavior's in ESS but its not quite the same, what is the limitation or design criteria/limitations we need to "watch out for".
F.i. If you run all the loads through the Victrons via AC1 for instance, how much load is that AC1 able to cope with ? Is that the 32Ah as Auxiliary port defined in the spec sheet of the MPII 5000 ?

ESSdynamic esspowerassist
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·

@VicTech_Power

If you have implemented the ESS assistant, power assist (as an option as you know) as a base feature is no longer a user defined setting. That is all the assistant when you set it is telling you.


ESS becomes the control. It being dynamic will determine when to power assist based on the user interaction in the settings in the ESS menu on the GX device.

The amount is assists changes based on

1. the battery level allowed to be used,

2. The input current limit and

3.the availability of solar.

4. Peak shaving if it allowed

So it is now very dynamic. (This is also the reason why some of the other base features cannot be set.) And can no longer a fixed value as it would be by the boost factor x.x that would be set normally under power assist.

If you have done smaller systems you will have seen all the principles in action.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
The AC 2 has a rating because it can be switched so also has a limited transfer amount.
The AC1 is not switched so really limited to the input current limit on the MP2 but ideally in system design you would only have the inverters load limited to max invert ability on only. As it will be overloading with no ability to load shed other wise.


A side note on most of the Victron range the input current limit is the inverter capability plus the limit needed to charge at full amps.

1 Like 1 ·
ejrossouw avatar image
ejrossouw answered ·

Not sure what you mean by technical as the manuals very much cover it although here is my summary.

PowerAssist is used in primarily used in mobile installations when hooked up to a limited shore supply. It uses batteries to boost the shore supply e.g. you have a 10A load and the shore is only 6A, depending on the sytem, it can top up the shore with 4A from batteries.

ESS is used for domestic fixed installs with a permanent grid supply. If you have an inverter that can provide 10A to loads, anything over, will be topped up from the grid. Typically the objective is to not use the grid supply. Transfer switch ratings have to be taken into when ACOUT is used for all the loads, although many domestic install only use the ACIN.

(D) ESS is still a work in progress and looks at various things such irradiance, consumption, best tariffs etc. to manage all the available energy sources e.g. charging when electricity is cheap and there is little sun etc. A bit bit like an automated version of an enduser manually setting charging schedules based on tariffs and the next days weather forecast.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

victech-power avatar image victech-power commented ·
Thanks @ejrossouw , but this is exactly NOT the answer I am looking for.

All you write is known to me.

I need to have the question amongst other answered :
Does the "function" power assist gets disabled during the ESS implementation or does the "setting" of the function power assist gets ignored ? Which is it ?

And the response I need I would like to have it techical and not like " the manuals say it all, because they don't !"

And either way : What are the design principles ? because designing for power assist is different then designing for ESS. But is there a design principle that deploys ESS whilst supporting

0 Likes 0 ·
ejrossouw avatar image ejrossouw victech-power commented ·

And there I was thinking it is quite obvious from the ESS manual. "The PowerAssist setting in VEConfigure3 will be disabled and ignored when ESS is installed.", but fair, this is then one for you to take up with your friendly Victron dealer if you require greater clarity. Simply put, it won't work with an ESS.

1 Like 1 ·
victech-power avatar image victech-power ejrossouw commented ·

@ejrossouw , please specify "WHAT wont work" ?? And do that technically please.


Further in the thread you see that @nickdb is writing that you can "pretty much recreate" PowerAssist behavior in ESS and my question is then... is that then true "powerassist" or not ?

Please technically explain " what it is that does not work".

0 Likes 0 ·
nickdb avatar image
nickdb answered ·

It is ignored as per the docs, it would need to be since ESS behaviour is opposite to that of power assist and you can pretty much recreate what it does via ESS settings regardless.

While you can still enable it via veconfigure, it won't do anything as far as I am aware.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

victech-power avatar image victech-power commented ·

@nickdb , you are getting close to what I would like to read, but you I am not satisfied by a statement like "you can pretty much recreate what it does via ESS settings regardless" and I also want Victrons confirmation.

Is the way you describe it Victron's PowerAssist or is it not ?
Or is PowerAssist as a word now more or less describing a behavior and not a designed technical solution ?

Let me put it differently to put you to the test:
If a customer wants a PowerAssist solution and we deliver an ESS setup ( as you say ESS pretty much recreates just that with all the load on the AC1 OUT ) is that then a correct design ?

0 Likes 0 ·