Hello everyone ,
Is there a gui mod that can show the relay control via temperature on the main display?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello everyone ,
Is there a gui mod that can show the relay control via temperature on the main display?
that's too bad. Can you let me take up your work Kevin...please
It is working here already as shown here for my Cerbo
If it is not, give me some details and I'll look into it.
Note: only relay 1 and 2 support setting to temperature alarm.
Thank you Kevin for your feedback.
My cerbo shows that only relay 1 supports the temperature. The circuit works via ruuvi sensor. “Overview” is also activated in the settings but there is no display on the main display.
Another error is that after restarting the system, the circuit is inactive and can only be started manually.
What data do you need for help?
CCGX, Venus GX and CANvu GX only have one relay. Please confirm what GX device you have.
If relay 2 appears in the Relay menu there is no way you don't have a Temperature selection. So please explain in more detail what you are seeing. A screen shot would help.
The relay page need to be enabled in Settings / Display & Language /Gui Mods. Show Relay overview must be on to see the relay Overview page. If you are not seeing this selection or if you aren't seeing the Gui Mods menu, then uninstall and reinstall Gui Mods and check again.
Thank you very much Kevin. The fault was the lack of activation of the relay function in GUI mods. but I have a big request.
Can you also install the on and off function (Temparatur) in the relay overview.
There is an on off switch in the settings for the temperature control.
I think you can insert the string into the overview display?
...... please
Unfortunately, that is not possible. The on/off selection is for each temperature device. So if you have two temperatures assigned to one relay there are two separate on/off selections.
I have 2 temperature settings on relay 1 but no selection in the overview
So if you have two temperatures assigned to one relay there are two separate on/off selections.
You yourself wrote that at 2 temperatures two on off switches appear. Did I misunderstand that?