Hey Yall,
So this is just the AC layout. Still in the works on DC but would like to install AC during December if possible. Plan on only running 30 amp in the US but want to ensure easy upgrades. All comments greatly appreciated!
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hey Yall,
So this is just the AC layout. Still in the works on DC but would like to install AC during December if possible. Plan on only running 30 amp in the US but want to ensure easy upgrades. All comments greatly appreciated!
You show two 30 amp shore power connections. You can't combine these since you can't guarantee the two hot legs are on the same phase or even that the neutrals come from the same source. It is unsafe and against code. The only way to use two separate shore power connections is to provide separate paths (hot and neutral) from the inlet all the way to the loads.
If you parallel the two shore power connections and power just one of then, you'll have exposed pins on the other plug at 120 volts fused for 30 amps. That'll kill you.
You can't use a battery switch for 120 volts AC.
You can't combine the Multi output with the direct shore power connection. If your goal is to provide a bypass for the Multi, a switch that switches both hot and neutral between the Multi output and your shore power breaker is necessary.
A detailed wiring diagram showing all conductions and what's happening inside each box would be required for detailed review.
I suggest you consult with a licensed electrician that is familiar with boats and inverter technology (Victron experience highly recommended). If you get this wrong, you could blow things up or injure/kill yourself or dock workers. This forum is not really the place for critical review of designs and is actually against the guidelines. But we do try to help where possible.
Yes- I have a hired electrician who has just viewed the vessel. I have helped to wire homes and warehouses but never a boat so want to learn as much as possible. I learn best by reading then doing and learning from mistakes.
So the two 30amp's are plugged into a 50amp shorepower with a ponytail. If need be, I can just run 30amp since many marina's only have such (adjust within victron gx?). This is also for future upgrades if I need more amps for ac units, etc.. My reasoning anyway. I had the understanding this inverter was capable of such.
The battery switch for the 120 was to bypass the inverter if I needed to have serviced and could still run outlets, hot water heater, etc.
thank you again!
Additional resources still need to be added for this topic
39 People are following this question.
Victron Multiplus Ground Issue?
Can a GX access information if 2 Multiplus are on the same bus, but driving two separate AC loads
N/####/system/0/Connected Not accurate / changing & N/####/system/0/Ac/Alarms/GridLost
measuring separate AC power usage from inverter via VRM
Can setting low temp cutoff in BMV-712 stop AC converter charging?