We are installing the following system:
Multiplus II (48V)
MPPT 250/60 tr (DC Coupled)
BMZ ESS 7.0 Battery
CCGX
Using ESS Assistant
The inverter keeps on failing on low battery although battery is 58V. Battery SOC is 51%. At times it goes to Charger in Absortion mode but is not charging. How to get it in Bulk mode or to charge via the grid?
ESS Settings:
TAB: General
System frequency 50Hz
Shore current 50.0 A
Overruled by remote unchecked
Dynamic current limiter unchecked
External current sensor connected (see manual) unchecked
State of charge when Bulk finished 95.0 %
Battery capacity 157 Ah
Charge efficiency 0.95
TAB: Grid
Country / grid code standard Other: not compliant to any grid code standard
LOM detection AC input 1 Type B (safe)
Accept wide input frequency range (45-65 Hz) checked
AC low switch mains off 180 V
AC low switch mains on 187 V
AC high switch mains on 265 V
AC high switch mains off 270 V
UPS function checked
TAB: Inverter
PowerAssist unchecked
Inverter output voltage 230 V
Inverter DC shut-down voltage 37.20 V
Inverter DC restart voltage 43.60 V
Low DC alarm level 43.60 V
Do not restart after short-circuit (VDE 4105-2 safety) unchecked
enable AES unchecked
TAB: Charger
Enable charger checked
Weak AC input unchecked
Stop after excessive bulk unchecked
Lithium batteries checked
Use equalization (tubular plate traction battery curve) unchecked
Charge curve Fixed
Absorption voltage 60.75 V
Float voltage 60.00 V
Charge current 50 A
Repeated absorption time 1.00 Hr
Repeated absorption interval 7.00 Days
Absorption time 1 Hr
TAB: Virtual switch
Virtual switch usage Do not use VS
TAB: Assistants
TAB: Assistant Configuration
ESS (Energy Storage System)
*) System uses LiFePo4 with other type BMS
(This can be either a BMS connected via CAN bus or a BMS system in which the
batteries are protected from high/low cell voltages by external equipment.)
*) The battery capacity of the system is 157 Ah.
*) Sustain voltage 50.00 V.
*) Cut off voltage for a discharge current of:
0.005 C= 52.00 V
0.25 C= 50.00 V
0.7 C= 49.20 V
2 C= 48.00 V
*) Inverting is allowed again when voltage rises 1.20 V above cut-off(0).
*) Relevant VEConfigure settings:
- Battery capacity 157 Ah.
- PowerAssist unchecked
- Lithium batteries checked
- Dynamic current limiter unchecked
- Storage mode unchecked
Any advice for charger setup?