My system include multiplus II 48/3000, cerbo and 2 MPPTs.
I updated the inverter release to V506 yesterday.
The AES mode is not starting as it should.
find below details of parameters I have entered.
What can I do to solve this problem ?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
My system include multiplus II 48/3000, cerbo and 2 MPPTs.
I updated the inverter release to V506 yesterday.
The AES mode is not starting as it should.
find below details of parameters I have entered.
What can I do to solve this problem ?
Increase the 35W a bit higher. ( 50 or 70W)
Your inverter is pulling 1a at 56.46v that is almost 57W. Which is enough to keep it out of AES.
I know the AC is reading lower but the DC estimate is higher.
Hi Alexandra,
I don't see your point because, as you can see the setting for starting AES is already 69W and not 35 W (or is there anything I have not understood ?). Anyway, I followed your recommandation with new setting up to 80W. AES is not starting either. please find below new setting :
what can I do to solve this problem ?
Does it trigger with loads disconnected on the AC out.
I tried this afternoon to disconnect all the load.
The only load remaining on the multi was its own consumption indicated as AC out 17W
There was also the Cerbo taken 3W directly on the battery
the AC out stayed at 17W : I assumed the AES didn't start
The multi in this system is configurated for Soc calculation
Is the AES mode compatible with SOC calculation, VRM supervision or Cerbo connection ?