Hello folks,
I have a multiplus II 3000 (firmare v3.10) with two pylontech US2000C.
The pylontech BMS states that the "charge current limit" (CCL) is 50A but my multiplus never seems to go beyond 25A.
Initially I only had one battery and therefore I set 25A in VEConfig (charger / charge current). I tried to increase this value to 50 but cannot go beyond 35 in VEConfig.
I'm not even sure if it is really used, if a pylontech BMS is connected via CAN bus.
In the DVCC setting I played around with the "maximum charge current" setting, but this seems to be only applied if below 25A.
As far as I understand it, one pylontech should be only charged with up to 25A, but 2 can be charged with 50A. The BMS seems to send this information to the MP. But the MP seems to ignore this.
Is there some other setting that I missed?
Hope you can help me :-)
cheers Matthias