I have a switch wired across the aux input of my multiplus and an assistant which sets the charge current to 0A when the switch is closed (<1v) and to 90A when the switch is open (>4v).
I also have "disable charger when charge current should be zero" ticked.
This puts the multiplus into pass-through so that the batteries only charge from solar even when grid is available.
However I have noticed that every ten minutes or so the inverter goes into bulk or absorption charging mode rather than pass-through for a second or so and alternates back and fore a few times before going back into pass-through. this then repeats after another ten minutes.
It doesn't seem to actually allow much charge current through but is annoying.
Can anyone explain this behaviour?
I have tried setting the assistant to 0A if aux input voltage <2v, but same problem.
The multiplus seems to be over-riding the assistant.
multiplus firmware is 487.