Charging with a Skylla IP44 and Multiplus Inverter/Charger - is it safe?

I have a 110v 3k 24v Multiplus inverting/charging my battery bank. I'd like to add a Skylla IP44 charger - but if I do that, will the Skylla need to talk to the Multiplus or will I burn up the charger? I plan on adding an additional Skylla IP44 (30A 24V) also in the future, which I understand I can parallel to the other Skylla.


So can I run the Multi Charger and Skylla IP44 charger without issue or do I need to make a connection or settings change to do so safely?

battery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
JohnC avatar image
JohnC answered ·

Hi Miami. That'll be ok. They don't need to communicate, and will just follow their own charge algorithms.

They will work safely just connected to the same batt/dc bus, regardless of ac supply phases.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

miami337 avatar image miami337 commented ·

Thanks John. So to clarify, when I add a second SkyllaIP44 - do I need to connect them with the Can.bus and program them somehow to be in parallel, or will they simply follow their own settings as well? I just don't want to burn up the new chargers.


If I do need to get them in parallel, any idea where I can find instructions on how to do that properly?

0 Likes 0 ·