Cerbo GX V3.00 and after update to V3.01, System changes CVL from diyBMS

Hello everyone,

I noticed today with Cerbo version V3.00 that the BMS specifications of the diyBMS (CAN bus - Charge Voltage Limit CVL) are changed by the Cerbo system.

55.2V was set in the diyBMS and after activating the DC coupled PV feed in and limiting to 100/1000W, the CVL value changed to over 58V!!!! The diyBMS then opened the main contactor.

If I switch off the limitation, the CVL slowly falls to the set value of 55.2V.
After a short time the value rises to 55.4V and falls to 55.1V.

After the update to V3.01, the result was the same.

cerbo gx
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mrfrodo avatar image
mrfrodo answered ·

Dear Mr. @mvader (Victron Energy),

please notice my post above.

Thank you.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @MrFrodo,

We have to be very clear on this point that Victron offers no support for 3rd party DIY BMS systems.

It is fine to discuss in the modifications space, but please do not ask for help from Victron.

This is documented here on our battery compatibility guide.

cleanshot-2023-09-05-at-193706.jpg


0 Likes 0 ·
mrfrodo avatar image mrfrodo Guy Stewart (Victron Community Manager) ♦♦ commented ·

Dear Mr. Stewart,

thank you for fast answering.

When describing my problem, I hoped that people would realize that the problem was not the third party diyBMS, but the programming of the Cerbo GX.

The diyBMS does exactly what it should - and has for a long time.
If there were any problems, I also communicated them in their Github.

Now it's a Victron bug!

Apparently, the activation of the grid feed in, in combination with the power limitation, influences the charging system.
But that's exactly what it shouldn't do!
It must accept the values of the BMS - and it doesn't matter which BMS it is.

Please check this matter internally.

I would be happy to send you a video and provide you with information.

I know that Victron also has battery systems.
Unfortunately, these are about 4500€ more expensive with a comparable capacity.
This is probably why many people rely on other batteries and BMS systems.


0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ mrfrodo commented ·

The behaviour of the battery charging controls when enabling grid feed-in hasn't changed in any recent Venus releases.

It is documented in the GX manual that enabling feed in will override battery limits so that the MPPT will continue to produce energy once the battery target is reached to allow surplus for the export.

There are several systems that cannot accept this over voltage condition, usually due to using an unsupported and untested BMS, and then need to disable feed-in.

There are several posts about this behaviour on the community, but this is good one to start - https://community.victronenergy.com/questions/187320/dvcc-feedin.html