I have two MultiPlus 24/3000 70-50 (120V) in parallel. I also have a Cerbo GX. In Victron Connect (both units: Master/Slave) AC Input Current Limit, override by remote is disabled, and AC Input Current Limit is set to 6.0A. Power Assist is on. I also have the Charge Current set to 20 Amps on Both Units. AC Input Control is not currently enabled, but my intent is to set that up soon. Trying to limit variables while troubleshooting this parameter.
If AC Loads are zero, or minimal, the draw on the generator stays low (1400 watts or so), but as loads increase the draw on the generator increases, and will rise to over 2000 watts. Charging is held at 40 amps (combined), so that setting appears to be respected, but the AC Input Current Limit is not being respected.
Trying to set this up so that I can use a Honda EU2000 generator from time to time where noise is a factor, and it's not acceptable to run the big generator.
Any ideas how to configure the units so that AC Input Current is respected?