No matter what I check, if I lose the grid for even a second the entire system shouts down and takes forever to reboot and I get a HighDC Ripple error(seems to be corrected after I fixed the settings the update changed) and Overload L1 and Overload L2 even if the load is well below the max of the Multisplus’s.
I am running 2 Multiplus 12/3000/120v in split phase with 900amp hour batteries with a discharge capacity of 400 amp for 3-5s 12v batteries, I have checked and rechecked every connection line length.
Update,
Found that a firmware update changed a bunch of my settings in my inverters, so once I corrected that it seems that the High DC Ripple error might be gone, however the system is still shutting down and I believe the inverters that are in split phase are not doing a pass through on each line which is causing the load draw is causing my inverters to over draw my batteries and causing my BMS to shut down. Why would they not be doing a pass through? My single inverter did the pass through and I would never see overload issues unless the grid was completely down and the inverter had to draw from the battery.