question

rgear13 avatar image
rgear13 asked

Elecnova DDS1946-2M energy meter for cerbo gx?

Does anyone know if I can connect this energy meter and usb to rs485 cable with the cerbo gx?

captura-de-pantalla-2023-08-14-a-las-222202.png

captura-de-pantalla-2023-08-14-a-las-222353.png

captura-de-pantalla-2023-08-14-a-las-222405.png


meter:

https://www.amazon.com.mx/dp/B0B1ZXP5R7?psc=1&ref=ppx_yo2ov_dt_b_product_details

cable:

https://www.amazon.com.mx/dp/B0BJK8W5S3?psc=1&ref=ppx_yo2ov_dt_b_product_details

cerbo gxBluetooth Low Energy - BLE
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Dean Perry avatar image
Dean Perry answered ·

If you are trying to use it for a grid measurement or a PV inverter then you are probably out of luck unless it happens to appear exactly the same on Modbus as one of the Carlo Gavazzi or ABB meters: https://www.victronenergy.com/upload/documents/Datasheet-Energy-Meters-Selection-Guide-EN.pdf

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

matt1309 avatar image
matt1309 answered ·

Hi @rgear13


As Dean mentions you'd either have to hope the modbus output is the same as those two supported meters. Or if you're good at python you could probably analyse that meters modbus output and then create custom driver to implement into venus os/gx device.

It shouldnt be too difficult you could copy the python scripts for the existing supported carlo and ABB meters:

They can be found in the below paths of the venus os/gx device.

/opt/victronenergy/dbus-modbus-client/abb.py

/opt/victronenergy/dbus-modbus-client/carlo_gavazzi.py

And then you'd need to add the new version say you call it newMeter.py to the dbus-modbus-client.py document by adding


import newMeter


In regards to the cable it looks to be the correct chipset but I'm not 100% sure what other criteria is required regarding cables.


However it looks similar to this guys cable who had to tweak something in his:

Energy Meter ET112 Not seen by Cerbo GX - Victron Community (victronenergy.com)



EDIT: If you go the route of making custom python script you may have more success moving the question to Modifications section of the forum.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rgear13 avatar image rgear13 commented ·

I'm going to investigate the python issue, thanks for your answer.

0 Likes 0 ·