MultiPlus 48V 8000 Low Battery Alarm

Hi everyone. I have a Victron MultiPlus II 48V 8000 inverter as part of my solar system. Its mostly there to invert with a small requirement to charge from the grid on dull days.

Its connected via the VE-Bus to a CebroGX. I have a RS MPPT 450/100 charge Controller managing the solar panels. And I have RosenPV 48V batteries (2 10Kw pakcs).

Initially when I installed the MultiPlus inverter it took the Battery charge state from the RS MPPT charge controller. However I wanted to harvest data from the Victron gear into a home automation system (Home Assistant) that is on the same network as the CebroGX.

So I followed the installation guide to add an assistant to the MultiPlus (the ESS assistant). This is required to open up the MQTT port that Home Assistant can monitor and receive data via.

I did have to create a custom battery profile in the MultiPlus' Charger setup, but I used the same settings as the RS MPPT charge controller has.

Now when I switch on my MultiPlus Inverter, it throws a LowBattery alarm and turns itself off.

Here are a few phots of the main screen for my set up.

low-battery-alarm.jpg

cebrogx-multiplus-screen.jpg

multiplus-config-general.jpg

grid.jpg

multiplus-config-inverter.jpg

multiplus-config-chrager.jpg

I created this RosenPV Battery profile, but copied the setting from my RS MPPT 450/100 charge Controller, which work fine there.

multiplus-config-vurtualswitch.jpg

Virtual Switch is off otherwise you can not install any assistants

multiplus-config-assistants.jpg

This ESS assistant is required for MQTT connections to be turned on.

multiplus-config-ve-bus-monitor.jpg

Not sure what this shows, I added it for completeness.


Can anyone tell me where I have gone wrong?


Kind regards


Duncan




Multiplus-IIess settings
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
seb71 avatar image
seb71 answered ·

For 16-cell LiFePO4 a battery voltage of 49.84V (under no load/no charging) is close to empty.

When using ESS, the low voltage settings are those configured in ESS (which you did not list).

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duncangardiner avatar image duncangardiner commented ·

Hi @Seb71


Ok here are all the ESS settings I can find. Most are on the CebroGX.

ess-modes.jpg

ess-settings-1.jpg

ess-settings-2.jpg

The Configuration tool only lets me add the ESS assistant, it gives no means to add any changes. The Summary page I assume is guidance rather than my actual setup?


multiplus-config-assistants-ess-summary.jpg


Kind regards


Duncan

0 Likes 0 ·
Show more comments

Related Resources