Looking for a Cerbo GX relay port connector?

I was looking at configuring relay port #1 to turn on a couple small 12v computer type fans for cooling the electrical bay based on the temp from a probe. That looked fairly simple and I configured it. But when I looked into hooking up the wires from the fan I found what looked like a port with three connections that probably needs a special connector based on its shape. What connector is that? I will need to purchase one (or two) so I can wire them in. Also I didn't see a pinout diagram, there are three pins, Positive, Negative & ?? What is the third one for, doubt its another ground/negative. I am hoping i can buy them somewhere.. traveling in Alaska at the moment and my existing thermostat the ran the fans went kaput.

cerbo gxRelay
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
seb71 avatar image
seb71 answered ·

The connectors should be included:

https://www.youtube.com/watch?v=3wheKaU2_qw


The relay pins are labeled on Cerbo:

NO (Normally Open) / COM (common) / NC (normally closed).

So you use COM and either NO or NC, as needed.


It's not supplying power. Just open/closes a contact.

Check the Cerbo manual for the maximum voltages and currents for the relays.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Bill avatar image Bill commented ·
Thanks for that pin out info. I will go back and see if I can find that in the newest manual I downloaded the other day to figure out how its used. It did say it had 12v power and up to 6 amps. The two fans are a total of .84 amps (.42 each) so the way I read the manual it would be fine powering them. Are you saying that it cannot and I need to find another relay for that little power?
0 Likes 0 ·
Show more comments
pwfarnell avatar image
pwfarnell answered ·

If you have lost them or they were not left by the installer there is some info in the thread below.

https://community.victronenergy.com/questions/81143/terminal-block-for-cerbo-gx.html

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Bill avatar image Bill commented ·
That thread only speaks to the terminal blocks. There is no actual Relay connector info except try to find an installer. I am in Tok Ak today and heading into the Yukon in the morning. Maybe I can find an installer in Whitehorse in a couple weeks. Bummer. Lots of dry camping between now and then. Mine appear to have been lost after installation a couple years back.