Just purchased a Victron system to upgrade my AS-installed Solar system. Have 4 LiFePO4 house batteries, 100Ah each in parallel. Not setting it up to run Air Conditioner, just need to camp off the grid BUT with enough battery storage to run my CPAP for 3 nights. Only have 2x80w panels on the roof but will upgrade them shortly. Function, get into NC State Park campsites w/o power sites.
Purchased MP-II 12/2000/120-50 120v, Lynx, 712 Battery Monitor, MK3-USB-C, VE Bus Smart Dongle. Keeping for now the MPPT 150/35 AS installed.
If you know the AS Basecamp 16 you know it is only 16' 2" and the compartment I have is beyond tiny to get all of the gear into. Batteries are stacked two high of 2 columns. The distance between the batteries and the Lynx is less than 3' and ditto the Lynx to the MP-II.
Question:
The manual on page 12 for my MP-II manual says 2x1/0 ("2x means two positive and two negative cables") for such a short distance with a 400A fuse.
I found a schematic here on the Victron site with far more gadgets than I need and NO suggestions regarding what size wires/cables to use for any of the DC circuits/battery interconnects.
As the space I have to work in only has access via a 13" w X 20" h opening, and I'm 6'4" and 220#'s, the lighter gauge wires to work with will be an asset. Given that V says on page 12, 1/0 does the job with a 400 A fuse, does everyone feel comfortable with that for battery connects and MP-II to Lynx connections?
Thanks,
Jack