Just purchased a Victron system to upgrade my AS-installed Solar system. Have 4 LiFePO4 house batteries, 100Ah each in parallel. Not setting it up to run Air Conditioner, just need to camp off the grid BUT with enough battery storage to run my CPAP for 3 nights. Only have 2x80w panels on the roof but will upgrade them shortly. Function, get into NC State Park campsites w/o power sites.

Purchased MP-II 12/2000/120-50 120v, Lynx, 712 Battery Monitor, MK3-USB-C, VE Bus Smart Dongle. Keeping for now the MPPT 150/35 AS installed.

If you know the AS Basecamp 16 you know it is only 16' 2" and the compartment I have is beyond tiny to get all of the gear into. Batteries are stacked two high of 2 columns. The distance between the batteries and the Lynx is less than 3' and ditto the Lynx to the MP-II.

Question:
The manual on page 12 for my MP-II manual says 2x1/0 ("2x means two positive and two negative cables") for such a short distance with a 400A fuse.

I found a schematic here on the Victron site with far more gadgets than I need and NO suggestions regarding what size wires/cables to use for any of the DC circuits/battery interconnects.

As the space I have to work in only has access via a 13" w X 20" h opening, and I'm 6'4" and 220#'s, the lighter gauge wires to work with will be an asset. Given that V says on page 12, 1/0 does the job with a 400 A fuse, does everyone feel comfortable with that for battery connects and MP-II to Lynx connections?

Thanks,
Jack

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
Kevin Windrem avatar image
Kevin Windrem answered ·

I don't find a MP II 2000 VA model but there is a Multiplus 2000 (not the Compact) in the same cabinet as the MP IIs.

The manual for the MP || lists wire size for the 3000 VA 12 volt model as 2x 1/0 AWG for up to 5 meters

The manual for the 2000 VA Multiplus (and the Multiplus Compact for that matter) requires one 70 mm2 = 2/0 for up to 5 meters and a 300 amp fuse.

I had similar install issues mounting batteries and Multi Compact under the bathroom sink in my travel trailer. I did manage to get 2/0 wires to where they needed to be. In hind sight, I should have removed the front of the cabinet for easier access. I'd recommend it if you have that option.

2/0 is 70 mm2 and an equivalent would be two #2 AWG (35 mm2) in parallel for each connection. Just keep the paralleled connections the same length if you go that route.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cleanlivin avatar image
cleanlivin answered ·

Kevin, YOU are correct! I meant to type in 12/3000!
My error - my excuse I'm coming down with a nasty cold! Sorry for the mistake!

First, No way can I get more access space. I have a small cavity with only 13w X 20h access hole that is in the front of the basecamp UNDER the bottom of the sink and drain pipe with the shower wall on the left, the frig on the entry hole wall and the 3rd wall the curve of the outside wall to the nose of the front trailer wall! LOL

"The manual for the MP-II 12/3000/120-50 lists wire size as 2x 1/0 AWG for up to 5 meters"
Yes, now is that 5-meter limit to be the cumulative distance of each of the positive and negative cables between every one of the 4 100Ah batteries terminals, over to the Lynx, then over to the MP-II terminals? Or just the distance of the longest leg (battery terminals of (+) added to distance over the the Lynx terminal since that is the longest length between any of the components?

So if the + total of battery positive terminals is 6 feet(1.524 meters) to just the Linx (+) terminal for only the (+) cable, AND the same for the negative cable = a total of both positive and negative of 3.5 meters I'm well under the <5 meter value. (Do I add both the positive leg and the negative leg distance of each together OR just the distance of one length of either the + or - cable to define that I am below the <5 meter value?)

Is that logic correct OR do I have to now add the cable from the battery terminals to the lynx to the MP-II and the cable from the Lynx to the frame ground too?

Yes, that is my confusion. I'm not a EE by any stretch of the mind - retired Nerd.
So my thinking is just a simple 30Amp AC system in the little Basecamp should not need 4/0 cable. 2x 2/0 at best for each current. Batteries will be two columns of two high each with EACH battery strapped to the floor with a separator board between each of the two in the stack.img-5387.jpgimg-5326.jpgimg-5350jpg.jpeg


img-5350jpg.jpeg (808.2 KiB)
img-5326.jpg (2.1 MiB)
img-5387.jpg (2.2 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cleanlivin avatar image
cleanlivin answered ·

Here is a copy of part of my spreadsheet I built to calculate my Ah's needed:

ah-used-wo-o2-concentrator.png


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image Kevin Windrem commented ·

That looks like a challenging installation. Getting to the battery terminals of the top two batteries will be difficult. Remember that the battery wires will be live and a short could blow fuses in the Lynx. Also, a blown fuse might require removing the batteries to get to the Lynx. If at all possible, I'd find a way to relocate the Lynx so you can get to it with the batteries in place. That way you a leave the fuses out while wiring. Mounting the batteries on their sides might also help with access.

You need to consider the total length from battery through the Lynx to the MP II. If you run separate wires from each battery to the Lynx and keep them all the same length, then these can be 1/4 the total size. 2/0 is 70 mm2 and you need two of them to the MP II so a total of 140 mm2. Each battery to Lynx connection could then be 140 / 4 = 35 = #2 AWG.

The underlying issue is two fold and both conditions need to be met:

1) ampacity of the wire needs to handle the maximum average current to keep the temperature below the insulation rating.

2) voltage drop at the maximum peak current.

There are charts and calculators on-line that can give you the numbers once you know the cable lengths.

1 Like 1 ·
cleanlivin avatar image
cleanlivin answered ·

To add to the "joy" of this project, my lady few Delta from Seattle to RDU two weeks ago. She had a direct flight, sat on the tarmac for 5 hours in the plane, was put back in the terminal till the next day, and flown to ATL to catch another flight to RDU. Talk about a breeding poll to dive into to catch a virus!

We are now fighting a very nasty virus together and I'm way too weak to work on the trailer. Glad I'm retired! As bad as this is, figure I have 4 more days of misery left.

Now I understand and have been told that I only need a 2000 watt inverter, but MPII is not offered as such BUT you can in the setup limit the input load to only 2000 watts! Thus that would disable the other 1000 watts the inverter is capable of producing making the cable load less and a smaller Amp fuse in the + line to the Lynx the better choice over the 400Amp? (https://community.victronenergy.com/questions/85286/does-the-multiplus-3-kva-invertercharger-allow-me.html) You need to scroll down quite a ways to get a clean definition.

---------------
First, I'm confused in more ways than one.
I found a chart that shows for one 1/0 cable rated at 167F takes a 150A fuse and rated at 194F takes a 170A fuse.
But IF I run two 1/0 what would be the proper size fuse?
And if I mate both of the 1/0 cables at and from the Blue Sea + line Fuse block is it the same?

---------------

Just dragged this aching body to the Basecamp 16X, as best as I could. Measured the distances:

Parallel connect each pole of the battery terminals will be 70" for each + & -.
From the last in the chain to the lynx and then to the MPII terminals will be at 116", again for each + & - cable

For only one current, say +, I need 186" of cable = 15.5 feet.

The manual says can run two 1/0 cables up to 5 meters total length, or 32 FEET!

Thus IF what I have said for a single cable is correct of 15.5 feet I am well below the 32-foot limit.
------------
Here is were I get confused. I read at one DIY site that you must ADD the total length of the + cable to the total feet of the negative cable to use to determine the cable size.

Is that true?

Even if true, I would only be at the upper limit of just 2 x 1/0 cables, and thus for buffer should I to a 2/0 cable of two strands per pole/connection point just for added safety?

Sincerely appreciate any help educating this retired 77-year-old computer Nerd (Cray & SGI Super Computers).

Best,
Jack

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cleanlivin avatar image
cleanlivin answered ·

I have purchased all of the electronics, batteries, etc and now will install/place the batteries and start linking the electronic components together.
Here is my schematic and I would appreciate your review and offering corrections that you suggest! The 2x2/0 cables are per the factory manual, but all of the other cables as well as fuse sizesare open to review.

JFB 16X Electrical Design.png


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cleanlivin avatar image
cleanlivin answered ·

PS: In particular, should I run 2 x 2/0 cables to the frame ground or is one more than adequate?