I have the following equipment:
Multiplus II 5kVA (Firmware 505)
Cerbo GX (Firmware v2.94)
Bluesolar MPPT (VE.CAN type) 150/85 (Firmware v2.05)
Bluesolar MPPT (VE.CAN type) 150/70 (Firmware v2.05)
Energy meter ET112
LiFEPO 4 battery (without BMS that interfaces with Victron system)
I want to report a problem with Cerbo Firmware v3.0 and up. When I updated the Firmware on the Cerbo to v3.0 and the latest version, the MPPT's did not respond to settings in order to minimize grid usage. It only charged the battery according to the battery SOC, the went into "sleep" mode.
It does not matter what ESS setting you use. It only responds to battery SOC and ignores the grid requirement, in other words, you use energy from the grid while the MPPT's do nothing.
I did set all the VE.CAN settings correctly after updating the Firmware. I adjusted almost every setting imaginable, but it does not work.
When I booted with Firmware v2.94, everything worked again as it should. My conclusion is that there is an issue with Firmware versions from v2.95 and up regarding MPPT's connected with CAN BUS.