Need some help to understand following :
Configuration:
-1 x Quattro 10000 V505
-3 x Pylon 15 KWh
-Cerbo V3.01
-ET112
-NO PV
-Grid Set-point
ESS Peak Shaving and batteries charging scheme Implementation
Reason for help is as follows:
System works fine . As Loads peak demand are larger than Grid Setpoint, Inverter start to assist and load is served both by grid at setpoint and Inverter/ batteries, until load demand reduces, or SOC from batteries achieve lower configurted SOC% .
At this point Grid starts to serve 100% of load demand, regardless of Grid setpoint, what is OK.
But the point is that I was expecting that Grid will also start to charge batteries, so to have them fully charged before loads demand peak shaving back again.
One way to cope this is opening a Charge Schedule Window to charge batteries during the night, but it doesn´t solve the problem of multiple load peaks during the same day.
How to allow Grid to serve loads and charge batteries at the same time, during the peak saving period, when SOC has achieved lower limit, instead of only serving loads. Scheduled charging is not the answer , because we cannot anticipate when the extra loads will be there.
Thanks