question

Juraj Nikolov avatar image
Juraj Nikolov asked

ESS two instalation one works fine one not

Hi,


Why in one instalation i have Multi managed from external control and another with bulk ?

during installation 2, it doesn't matter how the charger is set on the inverter, whether it should stop charging at 30% or 95% ... the inverter was replaced and it has no effect ... what a magic :D

istalation #1

1690271640107.png


istalation #2

1690271673063.png




1690271917155.png


ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Juraj Nikolov

Same firmware, same batteries? Same programming? Same firmware on the batteries?

It would seem on the bulk one the Pylontec is not the controlling bms.

You could check that in settings. If it is not that then swap the master battery.

In short the problem is because the battery has not taken control you need to find the source of the break on communication. There is a difference between the systems you need to find it as the installer.

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
I have said this because there is a smart shunt in the second system. And they both do SOC. So a conflict.
0 Likes 0 ·
Juraj Nikolov avatar image Juraj Nikolov Alexandra ♦ commented ·

@Alexandra

It's not 100% the same.
The batteries are U3000C only in one installation there are 2 pcs and in the other 4 pcs.
Mppt is in one installation 1 pc 250/100 in the other 3 pc 150/45.
venus is 3.0 in one and 3.18 in the other (wase the same thing from 2.96 to 3.18)
As for the smartShunt, it's just like a different gauge, the measurement is set from pylontech, I tried disconnecting the smartshunt and it working exactly the same, so it doesn't affect whether it's connected or not, so at least I didn't notice it.
As for the battery firmware, I have to make a converter so that I can plug it in via RS485 and compare it.

And another difference is that the multi with ex.control does not have the upgraded MK3.

But I upgraded it gradually, with the vision that it will start working after the upgrades :) ... hmm not :)
I will try to reinstall it in GX OS, that is another option, maybe it will help, maybe not, who knows...
That one installation is behaving very strangely...

1690292138780.png

1690292177200.png


This is only for vysibility not for measuring.

1690292656939.png


And Ve.config is the same ... :)

0 Likes 0 ·