ESS two instalation one works fine one not

Hi,


Why in one instalation i have Multi managed from external control and another with bulk ?

during installation 2, it doesn't matter how the charger is set on the inverter, whether it should stop charging at 30% or 95% ... the inverter was replaced and it has no effect ... what a magic :D

istalation #1

1690271640107.png


istalation #2

1690271673063.png




1690271917155.png


ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Juraj Nikolov

Same firmware, same batteries? Same programming? Same firmware on the batteries?

It would seem on the bulk one the Pylontec is not the controlling bms.

You could check that in settings. If it is not that then swap the master battery.

In short the problem is because the battery has not taken control you need to find the source of the break on communication. There is a difference between the systems you need to find it as the installer.

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
I have said this because there is a smart shunt in the second system. And they both do SOC. So a conflict.