Admittedly, this is my first Victron install, and I appreciate all the help so far. I have my system up and running, but have not load tested it yet. I have 120V on each leg and 240V when tested from L1 to L2. Everything seems to be working as expected.
My question is about the AC wiring, and if it is OK to wire it as my diagram shows in the attached pic. The isolation transformer is about 1 meter from the Quattro's. The mains input is about 4 meters from the inverters. I wasn't sure if I need jumpers between the inverters for the neutral and the PE (both input and output), or if a home run for each as illustrated is OK. I thought it looked very clean with individual home runs, so that is how I wired it.
I have only worked with inverters that have built in 120/240 in the past, so the wiring on these is a bit different than I'm used to. I'm trying these out on my own boat, because I really like the custom programming and the integration with other systems. Thanks again for the assistance, any input is much appreciated.