chrishanvey avatar image
chrishanvey asked

Multiplus II - Physical Remote Switch for ON and Charge Only.

I am looking for a simple physical switch that can be installed to put the inverter into the "On" and "Charge Only" states. I am putting this inverter into a mobile work van and I would like for the operator to flip this switch on at the start of the day and then switch it off (Charge Only) at the end of the day. I do not want them to accidentally flip the inverter switch to "Off". Because some days they will also plug in the mobile unit to recharge their batteries overnight. If the inverter is "Off" charging will not happen. If I just left "On" all the time over the weekend or during a vacation they will likely come back to dead batteries.

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Mike Dorsett avatar image
Mike Dorsett answered ·

you can do this with a SPDT switch wired to the remote input for on/off/charge. If the SPDT switch doesn't have a centre 'off' position i.e.is bi-stable rather than tri-stable like the switch on the inverter, then the inverter will always be in one or the other modes.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrishanvey avatar image chrishanvey commented ·

Quick search, would something like this would work then?

https://www.digikey.com/en/products/detail/carling-technologies/V4D2GHNB-AAC00-000/483663

Also you say "wired to the remote input", but this green 2 pole dongle with a black wire jumper seems to be just an On/Off. (Pic below) Will I need to unplug the factory 3 way switch and extend those 3 wires to the new 2 way switch to get the charge only functionality?

remote-on-off.png


0 Likes 0 ·
remote-on-off.png (816.3 KiB)
Show more comments
Mike Dorsett avatar image
Mike Dorsett answered ·

Hi, yes, you will, or you could install the 2 wire BMS assistant and use AUX1 &2 to enable the charger or inverter, and leave the original switch in the on/invert position.

I forgot that the remote 2 way switch is unique to the multi-compact.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrishanvey avatar image chrishanvey commented ·

So I can program the inverter through their virtual assistant to use Aux 1&2 as On & Charge only? I just looked at this and it only say that it can force to float and disable charger, both options do not sound helpful. Is this just the wrong assistant or am I missing something?


screenshot-2023-06-20-121531.png

0 Likes 0 ·
mr-manuel avatar image
mr-manuel answered ·

You could also automate this completely with Node-RED in Venus OS large, so no need to flip any switch. Like turn to On at 7.00 from Mo to Fr. and turn to Charge only at 18.00 from Mo. to Fr.

You could also check the load and delay the button change, if it‘s beeing used.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrishanvey avatar image chrishanvey commented ·
Scheduling will likely not be very consistent to warrant this approach, however setting it to "Charge Only" after say 10pm as a fail safe to catch if some one forgot might be helpful. Though if the state is changed in software will this override what the switch says permanently, if I still installed a switch? Will it have to be one other the other and not both?
0 Likes 0 ·