I installed 4 victron charge controllers 250/100, 2 quattros and 3 lithium ion phosphate battery 10.3 kWh.
--> while the CC were charging the batteries I flip up the 250 A DC breaker of the inverter, the discharged capacitors inside the inverter causes the battery to switch off and than switch on. This also causes the controllers to stop producing, after a while two charge controllers start producing and the other two still not producing.
With a multitester, I check the pv output voltage when the CC PV breaker is off, voltage is 202.
And than when the breaker is on, the voltage reading is 0 volts.
3 strings of 5 solar panels in series.
VOC: 46.38 VOLTS
VOC correction: - 0.330 %V/ ⁰C
Lowest record temperature in "Bayonnais Haiti" is 10 ⁰ C
So Voc would be:
tempDiff= 10 -25 = -15
-15 × (-0.33 × 0.01 x 46.38) = 2.2853
Voc= 48.6758 Volts
String Voc = 5 × 48.6758 = 243.37 VOLTS