richie-gorrod asked

DVCC charge limit

Hello,

I have AC coupled and DC Coupled solar panels. (AC monitored with ET112)

4 x MPTT 250/85 on the DC side.

Multiplus 5000/24,

All connecting with VE can.

I have the charge limit set to 30a on the color control.

Not sure why I have a charge of 60a.

Many thanks,

Rich

dvcc 2.PNG

dvcc-2.pngdvcc-1.png


DVCC
dvcc-2.png (105.4 KiB)
dvcc-1.png (104.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
richie-gorrod avatar image
richie-gorrod answered ·

Hi Mark.

My ac coupled pv connects to my cu after the et112.

The grid comes direct in to the multi and then out of the multi into the cu.

Once the batteries are in absorption the ac pv does feed into the grid.

Many thanks.

Rich

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

richie-gorrod avatar image
richie-gorrod answered ·

Hi,

after doing some testing Alexandra is right the batteries are getting 30a from the AC coupled and 30a from the DC side of things.

Not sure if this is a bug in the software or is the system is working correctly.

My AC PV feeds in on the output of the multi.

Cheers,

Rich

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·
@Richie Gorrod

It could be that because o some misconfiguration the MP does not know about the MPPT chargers and you get CCL limit applied by MP and MPTTs at the same time.

0 Likes 0 ·
Show more comments
nickdb avatar image
nickdb answered ·

Is DC feed-in enabled ? If so that parameter is ignored.

All documented in the guide.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

richie-gorrod avatar image
richie-gorrod answered ·

Hi Nick,

Thanks for your answer.

DC Coupled is disabled.

Cheers

Rich

1686294741109.png


1686294741109.png (106.1 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·


In your picture you are probably charging 30A from grid charge (AC PV) and then also 30A from the DC mppts.

0 Likes 0 ·
richie-gorrod avatar image
richie-gorrod answered ·

ok thanks.

So the multi only controls the dc side of things.

Cheers,

Rich

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

It should control AC and DC side.

In mine does.

The only difference in my system is that my Fronius is on AC-IN side of MP-II.

The question is why your PV inverter is not feeding the grid. If for some external reason it cannot, its energy will go into the battery regardless of the DVCC CCL settings.

screen-shot-2023-06-09-at-102812-am.png

screen-shot-2023-06-09-at-103012-am.png

screen-shot-2023-06-09-at-103028-am.png

0 Likes 0 ·
richie-gorrod avatar image
richie-gorrod answered ·

Ok thankyou. Will double check and report back.

Many thank for the reply.

Rich

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

richie-gorrod avatar image richie-gorrod commented ·
All sorted. I forgot I had a charge assistant installed in the multi. It was to stop the charging of the agm cells if became out of balance.


Removed and all working as expected


Many thanks for everyone’s help

Rich


1 Like 1 ·