DC Grid Feed in at lower % Battery

Hello,

my system: Multiplus2 5000, Froniur AC 3phase, several DC charger, Lithium Battery without BMS connection.


It seems that DC-coupled PV - feed in excess start first 95% Battery, how to adjust to start maybe at 80% SOC? Or is a connection to BMS necessary? Or would the Victron Smart Shunt help to make the system run my way?


Thanks for your help :)

feed-in limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
cacer avatar image
cacer answered ·

i use a flow for nodered to set the gridsetpoint deeper if the weather over the day will be sunny and the battery is above 40%.


i found no other way to feed in early.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mitsch avatar image mitsch commented ·
You have also a AC System. So every second.. calculate.. earnings AC-consumption+DC Chargers= gridset point?
0 Likes 0 ·
cacer avatar image
cacer answered ·

Sorry. Just dc Solar.

My mp2 5000 was on full load when battery was full.

So i made a flow to feed in earlier when Solar forecast in the afternoon is high.

Now, on good days, i feed in from the morning, above 40% SOC.