ET340 and PV inverter on Victron output

Good day,


I have been trying to find the correct diagram with no avail,

I have a 45KVA Victron 3 phase system and a ABB Trio 27Kva on the output side,

The ABB has no communication to the Victron Cerbo, therefore i need to install an ET meter to see the PV production,

How would i wire the meter if it is 3 phase and i have the PV inverter on the output side,

Any info would be much appreciated,


Regards

Energy MeterAC PV Coupling
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
rnauschnegg avatar image
rnauschnegg answered ·

Why you are not doing like that: https://www.victronenergy.com/live/ccgx:abb_fimer?s[]=abb&s[]=inverter

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Gerrie Rossouw avatar image Gerrie Rossouw commented ·
This is a 27 Trio, which has no communication with Victron, i have tried, spoken to ABB as well.


Only the Trio 50 and 60 works

0 Likes 0 ·
rnauschnegg avatar image rnauschnegg Gerrie Rossouw commented ·
Ok, so just install the ET340 between the ABB and the Victron AC-out. ABB hast to be connected to L1 L2 L3 IN of ET340.



0 Likes 0 ·
rnauschnegg avatar image rnauschnegg rnauschnegg commented ·

Page 2...

https://www.victronenergy.com/upload/documents/Energy_Meter_ET340/113406-Energy_Meters-pdf-en.pdf