Configure ET112 as PV Meter on AC Out

Switched from a MP2 5000 Single-phase AC IN setup to MP2 5000 3 phase AC IN / AC OUT setup today. Using an ET112 on L1 as PV inverter meter usage. I cant change it from AC 1 to AC Out in Venus. When I select AC Out it jumps back to AC IN 1. Where my issue?

Energy MeterAC PV Coupling
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
marcmarin avatar image
marcmarin answered ·

Problem resolved, found the setting in a sub-menu of the meter.



1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rennmoehre avatar image rennmoehre commented ·
I have the same problem. Have you changed the setting in your venus device or directly in your meter?
0 Likes 0 ·
David avatar image
David answered ·

Which SUB menu please? We have the same problem. DPA

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason - UK avatar image Jason - UK commented ·
0 Likes 0 ·
1701992526435.png (23.9 KiB)
David avatar image
David answered ·

All good. There is a Sub Menu - Energy Meters. Thats where it is. Phew.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

David avatar image
David answered ·

THanks Jason. Much appreciated. Love Community.