Just wondering if this is s design feature or a problem
MP II 48/5000 230v
FW 459
ESS used VE BMS frequancy shift used for solar on/off 50.5 52.5 54 hz
with general flag set to ignor AC in
Venus GX 2.30
VE BMS used to control HV and or LV disconnect of the MP II
autostart turned on manually to have grid connected or disconected using relay assistants on AUX 1
AC sensor for Solar using assistant on Aux 2 - 5kw inverter and 4.5kw solar
Now it the HV error is triggered and the red LED is on on the VE BMS
and the grid then is disconnected by general flag and or a power failure
then it the grid will not reconnect again until the HV disconnect has been cleared, then it reconnects straight away
at the same time as the disconnect the Hz also raise and stay there at the high Hz value set with the Solar connection using frequency shift to disconnect
if you turn the MP II off and back on then it reconnects
if you turn the mains off again it disconnects
turn it on it wont reconnect (IF HV error is present)
Also as a side issue I am still haing HV issues when the Batteries are full a 1.5 amps is always being added to the batteries and its ESS related and I cant find a way to stop that I had a 58 volt event last night as well. just mentioned in case.its related in that area