When programming a relay assistant that changes the AC Out 2 relay with switch on and switch off conditions, does it totally ignore its original behaviour which is to be On after a 2 minute delay when AC Input is present?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
When programming a relay assistant that changes the AC Out 2 relay with switch on and switch off conditions, does it totally ignore its original behaviour which is to be On after a 2 minute delay when AC Input is present?
Yes; When AC2 out is controlled by an assistant the default behaviour is gone.
If you would also like the original behaviour as well, you can create multiple assistants to re-create it.
After looking through the forum, I couldn't find any solution and not wanting to clutter the place up with a new thread, Im' posting the question here. I have an electric car that I need to plug in on AC out 2 (240v) on a multiplus 5000. The rest of the trailer is on AC out 1. I would like to keep AC out 1 prioritized to use solar first, which I was able to do with assistants but now AC out 2 is no longer on and I'm having trouble figuring out how to set this up. What assistant should I use to accomplish this?
Any help would be greatly appreciated. =)I took another crack at it...
Still not getting it :( Everything works except turning mains back on when AC load is greater than 4000 watts. It over loads and restarts. Any one see what I'm doing wrong here