Multiplus AC2 output behaviour with assistants

When programming a relay assistant that changes the AC Out 2 relay with switch on and switch off conditions, does it totally ignore its original behaviour which is to be On after a 2 minute delay when AC Input is present?

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
victron-answers avatar image
victron-answers answered ·

Yes; When AC2 out is controlled by an assistant the default behaviour is gone.

If you would also like the original behaviour as well, you can create multiple assistants to re-create it.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bruce32466 avatar image bruce32466 commented ·

After looking through the forum, I couldn't find any solution and not wanting to clutter the place up with a new thread, Im' posting the question here. I have an electric car that I need to plug in on AC out 2 (240v) on a multiplus 5000. The rest of the trailer is on AC out 1. I would like to keep AC out 1 prioritized to use solar first, which I was able to do with assistants but now AC out 2 is no longer on and I'm having trouble figuring out how to set this up. What assistant should I use to accomplish this?

Any help would be greatly appreciated. =)
0 Likes 0 ·
1585076617417.png (16.8 KiB)
bruce32466 avatar image bruce32466 commented ·

I took another crack at it...

Still not getting it :( Everything works except turning mains back on when AC load is greater than 4000 watts. It over loads and restarts. Any one see what I'm doing wrong here

0 Likes 0 ·
1585082397403.png (21.9 KiB)
1585090408665.png (36.1 KiB)