question

huskkyenergy avatar image
huskkyenergy asked

Victon multiplus & Pylon us5000 issue

victorn.jpgHI,


I have a victron multiplus 48/5000/70-100 running on Pylon US5000 batteires x 2. We have updated firmware and installed the batteries as per the Victron manual making sure to use the ocrrect bus cables etc.


Our issue is the batteries where charging but now the system has gone into fault mode and displaying GX error #48 DVCC fault.

we have a cerbo GX on site and all was running well then with the extra sun the other day its sent the system into melt down mode.

We also have an external generator and second inverter connected to the system.

Any help is greatly appreciated.



Pylontechvictron
victorn.jpg (276.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

As per the manual, that is incompatible firmware. Update the inverters, chargers and GX to current code. Something isn't current if you get that error.

Without a wiring diagram and detailed inventory there's not much more to suggest.

(That is not a very neat looking installation)

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

huskkyenergy avatar image huskkyenergy commented ·
yea we didn't install we are picking this up from another installer who is no longer answering the phone. Cabinet for batteries not used, missing parts to star with its been a nightmare.


Victron unit was installed years ago by another installer and its a proper hash job.

Thank you for your help. we will try updating all components again.


0 Likes 0 ·
Show more comments

Related Resources

Additional resources still need to be added for this topic

Victron Pylontech battery compatibility guide