Updated Pylontech wiring

Victron has updated its Pylontech Wiring. See the picture below.

ds-pylontech-managed-lithium-battery-2021-3-11.jpg

In the version before, the GND cable was connected to the negative pole of the DC Distributor.


Now they have excluded the GND cable at the negative pole of the DC distributor. So the system is not grounded at the negative pole anymore.

Why did they change it?

Is it true, that the negative pole of the Battery is connected to Ground over the case Ground, as this fellow says:

https://community.victronenergy.com/questions/48804/pylontech-battery-earthing.html

I have read in the MPPT manual:

WARNING: WHEN A GROUND FAULT IS INDICATED, BATTERY TERMINALS AND CONNECTED CIRCUITS MAY BE UNGROUNDED AND HAZARDOUS.

So the MPPT should be grounded on the negative pole am I right?

Pylontechvictronschematics
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Cansin Sari

That is why the disclaimer is on the diagram - grounding varies according to region and battery manufacturer specifications. And the drawing is for illustration purposes mainly, what Victron does require for grounding for their equipment to work is illustrated.

So if your region or regulations wants negative grounding then that is what you do.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

Victron Pylontech battery compatibility guide