Battery not charging above 54v

I have system that will not charge the battery above 54v. Both the MPPT and charger settinga are set to 56v (absorption) , 55.5v (float).
I've tested the settings with running charge for many hours and tested the MPPT. At the moment I am unsure if the problem resides in the Victron of the Daly BMS?

MultiPlus-II 48/5000/70-48
Cerbo GX
SmartShunt 500A
SmartSolar Charger MPPT 150/35
Daly 16S BMS - LifePo4 Eve cells


I have checked the settings in VE Configure and the MPPT (VEconnect). is there any thing i can try to get a higher charge voltage?



Multiplus-IIMPPT SmartSolar
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image JohnC ♦ commented ·
@David Prentice

Is your battery still accepting current?

0 Likes 0 ·
Show more comments
3 Answers
Michelle Konzack avatar image
Michelle Konzack answered ·

Your values

56v (absorption) , 55.5v (float)

look very odd. AFAIK the

ABSORBTION must be HIGHER

or the

FLOAT be LOWER.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

david-prentice avatar image
david-prentice answered ·

Thanks for the response, the absorption is higher than the float. Am I missing something?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Michelle Konzack avatar image
Michelle Konzack answered ·

The difference between ABSORBTION and FLOAT is only 0,5V which can lead to this error.


Please read the Datasheet of your Batterie and correct the values accordenly.