Current mismatch

Victron multiplus 48/10000. DVCC off. Batteries request right now 51,8A. VE.BUS DC current only 13.4A. Does the inverter have any Settings that limit the current? There is also a case, in the low temperature environment (-15℃), the inverter after starting to provide the current needs a period of time to become large, this is normal?

Multiplus-II
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
DC current here is DC loads on the system. Not current to charge batteries

Please explain what you mean by battery request.


0 Likes 0 ·
brian-cn avatar image brian-cn kevgermany ♦♦ commented ·

Charge current limit (CCL): the maximum charge current requested by the battery.

0 Likes 0 ·
1 Answer
Galin Radoslavov avatar image
Galin Radoslavov answered ·

What kind of battery do you have?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

brian-cn avatar image brian-cn commented ·

51.2V100Ah Lithium Iron Phosphate Battery with BMS,BMS have been adapted to VICTRON's protocol

0 Likes 0 ·