The BMS has switch to Battery overcharge and the red led is on in the VE-BMS unit, now during the writing of this and switching the monitor bach to the BMV 700 the voltage reading has increased to 56.8v yet we are in float mode and the voltage should be going DOWN to 54.5 NOT UP
I have already had a runway voltage at 65 volts before and am suspecting that the voltage will just keep on increasing
now if I remove the OVER voltage condition and reduce the charge voltage back to 56V then the over voltage condition issue is removed from the VE-BMS then things return to normal
MP II FW459
Lithium LIPO 20Kw battery bank
Venus GX FW 230/50
BMV 700 FW 3.10
VRM fully active
ESS active
AC sensor ACTIVE
grid conected
Grid tie solar active as per the screen shots.
79watts and 1.7 amps still being added (per BMV700
Settings has DVCC turned on
voltage NOW 56.8V amps 1.6 BMV700
switch monitor to multiplus Voltage 56.8 amps 0.0
VOLTAGE NOW 56.9 on the multiplus amps 0.0
switch back to BMv voltage 56.9 amps 1.6amps
SO in Summary
it seems that if the VE-BMS is triggered with a OV protection and the red LED comes on then the charging on the MP2 does not fully stop it continues to supply about 1.5 amps and as the lithium's are full the voltage just keeps going higher
well thats my interpretation so far.
The below is the VE config setting in the Multiplus II
The below screen is with the Multiplus selected and its showing ZERO amps going in and the voltage is down at 54.7
Below Screen capture is with battery monitor BMV 700 selected and it shows a small charge going into the batteries of 1.5 amps