question

felr avatar image
felr asked

ESS oscillates between charging and discharging

In my ESS system, the maximum inverter power is externaly set to 0 W when a certain SOC is reached to prevent further battery discharge. In the range between 100% and 60% this regulation worked without problems. As now slowly more sun is available again I have lowered the limit to 50%.

Now a strange behavior shows up here:

If the limit value is reached, the inverter switches off as configured. At the same time, the Multiplus starts to charge the battery with 100-200W from the grid, so that the limit value is exceeded again after a short time and the inverter switches on again. Thus, the system oscillates between discharging and charging for hours.

1677928536287.png

1677928565378.png

Why does the MP charge from gird at all when ESS is set to Optimized (w/o Battery Life)? The battery voltage never falls below the low voltage threshold and the SOC never reaches below the ESS minimum SOC. Do you have any idea how to prevent this behavior?


Multiplus-IIbattery chargingESS
1677928536287.png (22.9 KiB)
1677928565378.png (41.6 KiB)
7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
What do you have your dynamic cut off set to? You could be triggering sustain? Or something like that producing the weird behaviour.
1 Like 1 ·
felr avatar image felr Alexandra ♦ commented ·

Thank you for this tip. Just checked my configuration. I'm using Pylontech LFP batteries, which are configured according to the Victron support document to a float voltage of 46V for all discharge currents. The voltage during periods with this issue is always above that.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ felr commented ·

Pylons float at 51v and have a dynamic cut off of 46v or at least i assume thats what you mean. Are the cells relatively balanced then? When was the last time they were at full charge?

And the pylontec is not changing its signal for charge and discharge?. My thinking is there is conflicting signals somewhere anyway.
0 Likes 0 ·
felr avatar image felr Alexandra ♦ commented ·

Yes, with 46 V I meant the dynamic cutoff voltage. Got somehow mixed up during translation.

Last full charge was two days ago and the cells are well balanced (no cell voltage difference below 90% SOC and above max. 30 mV). Since then the battery voltage never went below 48 V.

The pylontech batteries recognize the changing current flow direction almost instantly and switch their state from discharging to charging and back accordingly. So I don't think communication between the batteries and the Cerbo unit is an issue here.

If I externally send the Modbus command to disable the charger in the Multiplus units, charging stops. After enabling it again the oscillation continues.


0 Likes 0 ·
felr avatar image felr Alexandra ♦ commented ·

Another idea: In my configuration "Has DC System" is enabled as I do have some DC loads (about 40W). When Max Inverter Power is set to 0, does the system try to power the DC loads from grid instead of the battery? This could explain the low-power charging.

0 Likes 0 ·