ESS oscillates between charging and discharging

In my ESS system, the maximum inverter power is externaly set to 0 W when a certain SOC is reached to prevent further battery discharge. In the range between 100% and 60% this regulation worked without problems. As now slowly more sun is available again I have lowered the limit to 50%.

Now a strange behavior shows up here:

If the limit value is reached, the inverter switches off as configured. At the same time, the Multiplus starts to charge the battery with 100-200W from the grid, so that the limit value is exceeded again after a short time and the inverter switches on again. Thus, the system oscillates between discharging and charging for hours.

1677928536287.png

1677928565378.png

Why does the MP charge from gird at all when ESS is set to Optimized (w/o Battery Life)? The battery voltage never falls below the low voltage threshold and the SOC never reaches below the ESS minimum SOC. Do you have any idea how to prevent this behavior?


Multiplus-IIbattery chargingESS
1677928536287.png (22.9 KiB)
1677928565378.png (41.6 KiB)
7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
What do you have your dynamic cut off set to? You could be triggering sustain? Or something like that producing the weird behaviour.
1 Like 1 ·
felr avatar image felr Alexandra ♦ commented ·

Thank you for this tip. Just checked my configuration. I'm using Pylontech LFP batteries, which are configured according to the Victron support document to a float voltage of 46V for all discharge currents. The voltage during periods with this issue is always above that.

0 Likes 0 ·