Hi,

I've just fitted a Multiplus II ESS system at home with 4 off the Pylontech US5000 batteries and it's working beautifully. We have a Britwind 5kw wind turbine supplying power to the house via an SMA Windy Boy 5000 inverter. I have set this up on the critical loads AC1 out so it can supply power to the house even when we get a power cut which happens fairly often where we are in the Highlands of Scotland.

We have a power cut at the moment and I am a little concerned what will happen once the batteries have fully charged. Normally any excess electricity would just bleed back into the grid but as the grid is isolated I am unsure what will happen once the batteries get to 100%. Will the inverter cut it's output, will bad things happen?

I should add that the Windy Boy is around 10 years old and does not communicate to the Cerbo GX.

I can just isolate the Windy Boy manually from my system and then it will shut down as it used to in a power cut but obviously I may not always be on hand to do that in the future.

Can anyone let me know what happens if a 5kw inverter output has nowhere to go?

Thanks, Barry


Multiplus-IIHydro and Wind Power
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
ojack avatar image
ojack answered ·

The Multiplus will increase the frequency on ACout1 to make the inverter shut down. If the windy boy supports this it will be ok. If not you should cut the windy boy manually.

In future and if windy boy can not cut of by increasing frequency you could place a Relais between windy boy and ACout1 and control it by the cerbo depending on SoC.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

minor-problem avatar image minor-problem commented ·
The power remained off for a few hours so I was able to see the Multiplus doing exactly that, when the output from the Windy Boy was more than the AC loads and charging requirement combined the WB has detected a frequency disturbance from the MP and shut down. A very useful feature.


Thanks for your help!

0 Likes 0 ·
sharpener avatar image
sharpener answered ·

If you have an 8kVA Multi or larger you are OK, if not search for "1:1 rule" and see also this thread.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ojack avatar image ojack commented ·
Why Multi 8000? Windy boy 5000 is 5000VA = Multi 5000 is also 5000VA.

This should work i think.

0 Likes 0 ·