Ferrule or not? 10 AWG, 7-strand, PV wire into MPPT RS 450/200

I didn't see anything in the manual that mentions ferrules (although the manual does have a graphic that might indicate ferrules if those yellow ends of the wire are an indication), and opinions online seem to be all over the place. Right now I'm leaning toward not using ferrules because it's 7-strand PV wire, but I really have no idea. I have the ferrules and the tool, just don't know whether it's best practice in this case to put ferrules on or not. Many thanks for any thoughts!ferrule.png

mppt rs
ferrule.png (339.2 KiB)
9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

UPDATED POST - This post used to provide a definitive advice not to use ferrules with Victron MPPTs.

I would now recommend reading the discussion here for more up to date information and some nuance - https://community.victronenergy.com/t/using-ferules-pros-and-cons/1301

There is a concise instruction on when and how to use ferrules in Victron's Wiring Unlimited Guide - Electrical Connection chapter 10

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

waninae39 avatar image
waninae39 answered ·

yes

i always use ferrules for most of my connections

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

thomasbest avatar image
thomasbest answered ·

We’ve been digging into this issue a bit on the diy solar forum. Maybe a sliding gate grip does better without a ferrule. But the documentation and guidance on what wire treatment is appropriate under what circumstances is lacking in the product specific Victron documentation. Surprising for Victron to fall down on this important detail.


Any chance for some formal guidance to include a consult with the engineering staff?


See: https://diysolarforum.com/threads/source-to-buy-quality-wire-ferrules.60670/">https://diysolarforum.com/threads/source-to-buy-quality-wire-ferrules.60670/






2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

honu avatar image
honu answered ·

Strange that victron say : do not use ferrule but a multi strand wire to maximise contact while their battery connector is....so...badly done on the rs450, the lug is supposed to be put over a nut....with near no surface contact.

Explain this rs450 double nuts situation...why the hell there is a nut there while the lug should contact with the maximum surface and the nut preventing this to happend...? I've read the documentation and no clue on how to use those 2 nuts, I removed both and put lugs in contact with the electronic board.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fideri avatar image
Fideri answered ·

@AlaskanNoob I think Wiring Unlimited says somewhere that fine stranded wire (they give an exact count which is not 7) is to be used for Victron and specifically says that don't use wire with a few strands.

Fideri

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alex Pescaru avatar image
Alex Pescaru answered ·

Hi, @AlaskanNoob

Class 5 or higher stranding according to VDE 0295, IEC 60228 and BS6360.

Your cable is Class 2.

Although, depending on you panel configuration and current that passes through circuits, lower number of strands could be OK, as long as you provide a very good surface contact by properly crimping the wires together.