question

alaskannoob avatar image
alaskannoob asked

Ferrule or not? 10 AWG, 7-strand, PV wire into MPPT RS 450/200

I didn't see anything in the manual that mentions ferrules (although the manual does have a graphic that might indicate ferrules if those yellow ends of the wire are an indication), and opinions online seem to be all over the place. Right now I'm leaning toward not using ferrules because it's 7-strand PV wire, but I really have no idea. I have the ferrules and the tool, just don't know whether it's best practice in this case to put ferrules on or not. Many thanks for any thoughts!ferrule.png

mppt rs
ferrule.png (339.2 KiB)
9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alaskannoob avatar image alaskannoob klim8skeptic ♦ commented ·

Oh great. We ordered 2800' of this stuff and had it shipped to Alaska. It wasn't cheap. Had no idea that there would be any issue with 600V rated direct burial PV wire.

0 Likes 0 ·
alaskannoob avatar image alaskannoob klim8skeptic ♦ commented ·
Any idea why Victron has that spec for PV wire running to the panels? Is it because of the connectors that the Charge Controllers use? If so, couldn't I just have my 7 strand cable terminate into an MC4 connector, then plug that into a shorter strand of many-more-threads PV wire that meets Victron's specs before it plugs into the charge controller?


If the reasoning is the "contact area" as the manual appears to suggest, then wouldn't this solution work?

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ alaskannoob commented ·

I would think that this MIGHT just transfer the issue to MC4, but if the wire is specified as compatible with an MC4 connector, then yes, 7 strand solar to MC4 and then MC4 with fine strand to MPPT would be a solution.

1 Like 1 ·
alaskannoob avatar image alaskannoob Guy Stewart (Victron Community Manager) ♦♦ commented ·

Sounds like this will be my approach then. Use the CB to transfer over to the approved wire for the charge controller for the positive wire, then MC4 to transition for the negative wire.

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ alaskannoob commented ·

@AlaskanNoob are you going to have a PV breaker next to the mppt?

Seems like an obvious place to switch wire types.

Make sure that the breaker's clamps can be used with your 7 strand cable.

1 Like 1 ·
alaskannoob avatar image alaskannoob klim8skeptic ♦ commented ·
Yes, I've got a MNEPV20-600RT circuit breaker between the PV arrays and each tracker on the MPPTs.


But it's a single pole, so it would just be the positive wire going through it. So I'm still going to need to figure out how to get the negative to switch over before going into the MPPT (I think) so I will explore MC4 connections to make that transition.

Plus an MC4 for 8 AWG wire perhaps will help me find some wire that has the number of strands required, so far the largest number of strands I've found for 10 AWG is only 19 strands.

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ alaskannoob commented ·

But it's a single pole, so it would just be the positive wire going through it.

That's kind of dangerous.

Imagine your + PV cable gets damaged and is leaking to earth. Now your - PV cable is - 450v in reference to earth. That's quite a spark should you disconnect the - cable from the mppt. Quite a heart stopper should you touch the - cable.


2 Likes 2 ·
alaskannoob avatar image alaskannoob alaskannoob commented ·
Since the area of connection seems to be an issue, with lots of strands of wire required to be plugged into the charge controllers, I'm going to guess that ferrules are NOT desired for plugging into the charge controller?
0 Likes 0 ·
6 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

UPDATED POST - This post used to provide a definitive advice not to use ferrules with Victron MPPTs.

I would now recommend reading the discussion here for more up to date information and some nuance - https://community.victronenergy.com/t/using-ferules-pros-and-cons/1301

There is a concise instruction on when and how to use ferrules in Victron's Wiring Unlimited Guide - Electrical Connection chapter 10

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alaskannoob avatar image alaskannoob commented ·

Thank you so much for this clarification. It's great to get it from Victron rather than dueling opinions elsewhere on the internet!

1 Like 1 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ alaskannoob commented ·
I’ll make some resources to demonstrate why.

Ferrules make for a much neater installation, but they limit the contact surface area.

In some cases this isn’t an issue, but in others it can be.

A square crimpted ferrule will be better than a loose round one over thick stranded cable, but all will be inferior to fine stranded cable inserted with care and then torqued correctly.

Failure of an MPPT due to insufficient contact at the terminals is all too common unfortunately, though many MPPTs are also installed without optimum contact and without issues as well.


Best practice is a clean job, with fine strand to spec, and maximum contact surface area.

1 Like 1 ·
Craig Chamberlain avatar image Craig Chamberlain Guy Stewart (Victron Community Manager) ♦♦ commented ·
Thanks Guy, there are so many people out there advocating for using ferrules that I was about to buy a 35mm ferrule crimper and some ferrules for my upcoming MPPT installation. In general I am a big fan of using ferrules, especially for AC work but I was a bit sceptical about the benefits for the MPPT use case. Glad I did my research!
2 Likes 2 ·
alaskannoob avatar image alaskannoob Guy Stewart (Victron Community Manager) ♦♦ commented ·

Would love to see these resources when you make them, especially if they show how to insert the cables correctly and any ways to measure or confirm it's been done correctly. If the resistance is the issue, it would be great to measure that if possible for peace of mind. We'll have 8 trackers getting 400V or so, in the middle of a large forest, and there is no fire department so anything you can make to help us get this right would be greatly appreciated!

Also, I had read that fine thread wire going into the terminals was more likely to have a thread break off and cause problems which makes sense so I suppose that is part of why you mentioned inserting with care. If there is any way to tell/confirm that inserts were done properly and no threads were broken that would be great. I suppose a way of securing the wires so they don't get tugged after the install and brad a thread might also be in order?

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ alaskannoob commented ·

Wiring should always be mechanically supported so there is no stress on electrical connections. That should not be debated.


The ferrules issue often is but with the rising clamp design and the use of fine strand it is not necessary on the Victron equipment.


1 Like 1 ·
todd-mitchell avatar image todd-mitchell Guy Stewart (Victron Community Manager) ♦♦ commented ·
fine strand cable is not suitable for, or available for, high voltage and current from PV string or combiner box. I think this advice is misguided imho . Lets say you have a 250/100 MPPT (or MPPT RS) with 30 amps incoming current. What outdoor fine strand cable do you think can be found at 35mm2 or 2awg? We would typically run copper Teck armored cable , I think the only instances where you will fine fine strand copper of this size suitable for the conditions will be on a sailboat or RV.
0 Likes 0 ·
alaskannoob avatar image alaskannoob todd-mitchell commented ·

We ordered this 10 AWG PV wire that should meet the strand specs (87 strand) for use with the MPPT RS:


https://bulkwire.com/solar-pv-wire-600v-ul-4703

0 Likes 0 ·
richardcordes avatar image richardcordes commented ·
Under victrons wiring unlimited section 4.3 says ferrules highly recommended. Can you show me were victron says otherwise. Thanks.
0 Likes 0 ·
Craig Chamberlain avatar image Craig Chamberlain richardcordes commented ·
It does talk about ferrules being recommended where a screw is clamping down on the wire and might "pinch on only a few strands" but the connections on the MPPTs use something more like the sliding gate arrangement you see on AC breakers and main switches. I can definitely imagine that clamping down on a ferrule won't achieve the same spreading out of the cable and thus won't maximise contact area as well as it would with the fine strand wire itself.
1 Like 1 ·
Show more comments
waninae39 avatar image
waninae39 answered ·

yes

i always use ferrules for most of my connections

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

thomasbest avatar image
thomasbest answered ·

We’ve been digging into this issue a bit on the diy solar forum. Maybe a sliding gate grip does better without a ferrule. But the documentation and guidance on what wire treatment is appropriate under what circumstances is lacking in the product specific Victron documentation. Surprising for Victron to fall down on this important detail.


Any chance for some formal guidance to include a consult with the engineering staff?


See: https://diysolarforum.com/threads/source-to-buy-quality-wire-ferrules.60670/">https://diysolarforum.com/threads/source-to-buy-quality-wire-ferrules.60670/






2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

honu avatar image
honu answered ·

Strange that victron say : do not use ferrule but a multi strand wire to maximise contact while their battery connector is....so...badly done on the rs450, the lug is supposed to be put over a nut....with near no surface contact.

Explain this rs450 double nuts situation...why the hell there is a nut there while the lug should contact with the maximum surface and the nut preventing this to happend...? I've read the documentation and no clue on how to use those 2 nuts, I removed both and put lugs in contact with the electronic board.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Justin Cook avatar image Justin Cook ♦♦ commented ·

As can be seen in the datasheet as well as the introduction video of the RS line, the bottom nut is intended to stay in place, the lug is placed on top of that, followed by the washer, the lock washer, and the final nut.


The bottom nut serves two purposes: it allows you to use an open box wrench underneath the lug so that you can put counterpressure on the assembly to ensure that you can properly torque the top nut without causing undue stress to the PCB, and it provides an airgap to allow for heat dissipation in the assembly.


This type of connection setup is not at all uncommon in high-voltage high-current applications, and so long as the lug size is appropriate to the stud size, there is no appreciable decline in surface area contact because not only the nut but in fact the entire stud is carrying the current.

intro.png

3 Likes 3 ·
intro.png (944.9 KiB)
honu avatar image honu Justin Cook ♦♦ commented ·

Hello,

That would be the other option, but in this case why the MPII do not have this configuration (2 nuts), why only the RS450 ?

A M8 is 8mm => Roughly 50mm2 surface but stainless steel have a 5x resistance vs Cu.... so why wanted to go through all those contact surfaces : Lug > Nut > Bolt > Board contact. There is no contact between the bolt and the lug.. near none.

There is something really not obvious here. But yes i agree that the mecanical resistance is better ...

About strands, i'm using regular 35mm2 cable,do not know how many there are... here is my 50mm2.

img-20240114-224502.jpg

e

0 Likes 0 ·
Fideri avatar image
Fideri answered ·

@AlaskanNoob I think Wiring Unlimited says somewhere that fine stranded wire (they give an exact count which is not 7) is to be used for Victron and specifically says that don't use wire with a few strands.

Fideri

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alaskannoob avatar image alaskannoob commented ·

I know the MPPT RS manual says to use many stranded PV cable. We ended up buying new cable with far more strands and we used that to connect our panels.

0 Likes 0 ·
Alex Pescaru avatar image
Alex Pescaru answered ·

Hi, @AlaskanNoob

Class 5 or higher stranding according to VDE 0295, IEC 60228 and BS6360.

Your cable is Class 2.

Although, depending on you panel configuration and current that passes through circuits, lower number of strands could be OK, as long as you provide a very good surface contact by properly crimping the wires together.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.