Volt drop when connecting mppt 75/15 to solar panel.

I have recently brought a solar kit. With a victon 175w panel and a victron mppt 75/15. Once installing it has worked for around 5 days. The last couple of days it produced nothing. Even though good sunny days


When looking into today I found the solar panel at 19v when testing disconnected from mppt. When introducing mppt it drops to around 13v. This causes the batteries not to charge.


Has the mppt failed?


Thanks

voltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
secessus avatar image
secessus answered ·

The Victron 175w panel should read ~23.7v when not connected (Voc) and ~19v at Vmp. Is it possible the panel is shaded?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

joshuaafc1 avatar image
joshuaafc1 answered ·

I don't think it's shaded as I have moved vehicle during the day to get different voltages. And when it's getting dusk the voltage is less.


Why when introducing the MPPT the solar voltage drops so much ?




Thanks

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

secessus avatar image secessus commented ·

Why when introducing the MPPT the solar voltage drops so much ?

Having nothing connected makes the panel run at Voc, the highest voltage it can. Connecting something like a controller will typically drop panel voltage. That is normal. The panel's voltage isn't normal.


I have moved vehicle during the day to get different voltages

Do you have a picture of this setup? Panel Voc really shouldn't change much in normal daylight. Panel current will change with different conditions.

1 Like 1 ·
Show more comments
joshuaafc1 avatar image joshuaafc1 commented ·

20230216-074236.jpg20230216-074213.jpg

With mppt charger and without connected

0 Likes 0 ·
Show more comments
joshuaafc1 avatar image
joshuaafc1 answered ·

I have also tested direct at the panel leads and voltage is the same. 19.8v

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejrossouw avatar image
ejrossouw answered ·

I will not discount the switch as a potential contributing factor or even a bad connection. After operation and some heat being generated, connections may be not as tight anymore, especially if the torque settings of 0.75Nm were not strictly adhered too. Is the MPPT still correctly set up for 12V?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

joshuaafc1 avatar image joshuaafc1 commented ·
Thanks for your response. I have checked connections and also disconnected at the mppt put them cables in connector blocks and tested voltage with switch on. And I have 19.8v. Also resistance is good and low through the switch.


Mppt is set up to 12v on victron connect app.

0 Likes 0 ·