Hi Victron community,
Is there a way to interface the Lynx Smart BMS 500 with an EasySolar-II GX? Is this possible via the VE.Bus port on the EasySolar? I have two Victron 12.8V smart Lithium batteries in this system.
Thank you for your help,
Aaron
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi Victron community,
Is there a way to interface the Lynx Smart BMS 500 with an EasySolar-II GX? Is this possible via the VE.Bus port on the EasySolar? I have two Victron 12.8V smart Lithium batteries in this system.
Thank you for your help,
Aaron
Provided your EasySolar-II GX has a fully featured VE.Can port - see footnote 23 in the Victron GX product range overview - then yes. If it is has a BMS-Can port, then unfortunately not.
Do not try to connect the Lynx Smart BMS to the EasySolar's VE.Bus port. VE.Bus is exclusively for VE.Bus devices.
Hi Stefanie,
Thank you for your fast response! Bummer :( It looks like I received the older version of the EasySolar.
Is the VE.Bus BMS V2 unit my best option given that I only have VE.Bus and BMS-Can connections on my unit? If not, then what do you reccomend is the best product to interface my Victron lithium batteries with the EasySolar?
Thanks again,
Aaron
I would say yes. Considering its functionality, especially communication with VE.Bus inverters/chargers and a GX device, it is the best option. But in the end it comes down to your system.
Did you see the BMS Overview, which explains the main differences between all available BMSes?
Hi @Stefanie (Victron Energy Staff) Apologies, I missed your response in the tiny 'Show' link.
Yes, I have looked through this BMS document. I am tempted to keep the Lynx Smart BMS, purchase a Cerbo GX, and then run the whole show that way. This probably sounds a little nutty since I'll have two GX devices, but this would allow me to keep the battery health information that the Lynx offers, which is of interest to me for this project.
Does the attached diagram make sense? Thanks again for all your help. I really appreciate it! -Aaron
Diagram is looking good - except for the VE.Direct link between the BMS and the EasySolar and the VE.Bus terminator.
Hope this helps.
I asked about disabling the GX in easy solar. Was told pull the covers and disconnect the wires to it. Haven't done it yet, not ready to install.
I took a look inside the EasySolar, and bypassing its internal GX board seems easy enough. I'll report back - I dont have my JST PH crimper here today to make the VE.Direct cable. 
I'm happy to say everything is working great now with the Cerbo GX! Here is what I did:
1) Removed the facepanel of the EasySolar.
2) Disconnected Power, VE.Direct, VE.Bus from the internal GX Board.
3) Connected both VE.Direct from the internal MPPT 250 and VE.Bus from the internal MultiPlus II Inverter to the Cerbo GX. I used one of the exterior VE.Bus jacks for the inverter.
4) Connected Cerbo GX power to the AUX connection on the Lynx BMS
Thanks again Stefanie for all your help!





My project is coming along nicely with all this awesome Victron equipment :)


EasySolar-II GX 3000 & 5000 product page