I tested my SolarEdge SE5000 HDwave response to the frequency rise. The battery was 100% and it still continued putting out maximum power requiring manual intervention with myself. Both technical notes from Victron and SolarEdge were followed. The Solar Edge technical team confirmed my settings were correct when I contacted them. They updated all firmware and it still doesn't work. So if you have a SolarEdge connected on the AC out you might find it doesn't work as advertised when you really need it to. For safe testing you can follow my answer to this question https://community.victronenergy.com/questions/184775/can-i-control-the-frequency-output-of-the-quattro.html so you are not running close to 100% SOC.

I would strongly recommend testing the response in island mode with a less than full battery to avoid damaging lots of equipment. Right now I am considering playing safe and moving it back to the input side of the Quattro.

MultiPlus Quattro Inverter Chargersolaredge
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
pedaaa avatar image
pedaaa answered ·

i wonder if Victron really wanted to throttle your SE?

Was throttling really required already? (battery voltage near CVL)

or was only SOC shown with 100% (but battery voltage has not reached CVL so far)

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

andy156 avatar image andy156 commented ·

The Victron frequency went to the maximum throttle figure of 51.2 for some time in order to try and lower the charge current. Eventually he BMS was demanding zero charge. The voltage spiked and hit the maximum allowed for the Pylontech. The frequency in the SolarEdge display matched that of the Victron. The country was DG (diesel generator). So I am sure of what I am talking about. I have it all graphed.

I have artificially increased the frequency and the SolarEdge doesn't respond in any way whatsoever.

0 Likes 0 ·
andy156 avatar image andy156 commented ·

Do you have a working Solaredge APS system? Did you have to contact SolarEdge to make any changes on their side?

0 Likes 0 ·
Show more comments
andy156 avatar image andy156 commented ·

Here I just forced the voltage to 51.0. I know it is different to the one in the Victron note. However the Solar Edge guys said it is only allowed to operate for the warranty to 51 in the uk which makes no sense as the grid control to 53.4 I've run with it for now. The frequency response is set from 50.2 -100% to 51.0 - 0% in the SolarEdgescreenshot-2023-02-08-at-133517.png

0 Likes 0 ·
Show more comments
pedaaa avatar image
pedaaa answered ·

what do you mean with "it has equivalent settings" ?


by default, no SE inverter has the required settings. I sure this is the same on your HD-Wave inverter.


by default, most SE models have this APS-Mode settings:

P0 = 50,2Hz - 100%

P1 = 51,2Hz - 100%


but you need to manually! change the P1 setting to:

P1 = 51,2Hz - 0%


can you confirm, that you have done this?!

I am not sure about this, reading throw your comments?!

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

andy156 avatar image andy156 commented ·
As in it doesn’t have an app like yours. It’s done scrolling through a menu on the machine itself. Yes I have done the settings as I have mentioned many times. Both the solaredge notes and victron notes have been followed to the letter. The firmware is correct etc etc Why won’t you believe me? I’m only putting this out so that people don’t damage their equipment.
0 Likes 0 ·
pedaaa avatar image pedaaa andy156 commented ·

just want to make sure, we are talking about the same, and all potential errors are ruled out.


As i know of installations that work great with SE, and also Frequency shifting working well.

But those are 3phase Setapp installations with Multiplus II

So i am pretty confident, that my setup will also work well. But i can report on that in some days.


I have not came across, your HD-Wave + Quattro Setup.

Maybe there is something different on those?!

0 Likes 0 ·
andy156 avatar image andy156 pedaaa commented ·
Fair enough. You made me go and double check for the 8th time haha. It is still showing zero on the P1 value. I was wondering how many people actually test the frequency response? Neither document calls for it. The only testing mentioned is to make sure that the relay is changing the grid code. And then it seems to be assumed that it will work.


Have you actually seen the frequency response happening at the other installation or merely the relay switching the mode? I have so many panels now that the battery will fill up 4 hours on a sunny day now. 15kW going into them at max output. I need to know this is going to work as in the event of a power cut I am very likely to be with in the dangerous parameters of a full battery and high feed in to the grid.

It is strange and disconcerting since it is a menu option on the SolarEdge and the firmware offers it. When I hear back from the SolarEdge technical team I will post the results here.

0 Likes 0 ·
pedaaa avatar image pedaaa andy156 commented ·
yes, thanks, please keep us posted.

And i will also reply here once really field tested

0 Likes 0 ·