I'm looking for an 80A anti Islanding solution. The largest I can find is Victron's 63A, but that won't work here. What's the solution on a larger connection? Install a relay?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I'm looking for an 80A anti Islanding solution. The largest I can find is Victron's 63A, but that won't work here. What's the solution on a larger connection? Install a relay?
You can buy the Ziehl separately and build your own based on the 63A design but with the 80A switchgear.
Anti-Islanding Box 63A single and three phase Product Page
Ziehl Voltage and Frequency Relay UFR1001E Product Page