My multiplus 2 24/3000/70 wont charge from the generator - if connects, then instantaneously disconnects wiht a low voltage error in the IP protection log. This is strange because the generator voltage is steady at 235 - 240V, frequency is 51.5Hz and the scope shows no strange shape to the sinewave. VE cofigure VE bus monitor shows the correct generator voltage and no surge or other noise from the generator is heard as the inverter connects and then rapidly disconnects. The retry time is about 1 minute, then 2 minutes and gets longer. An AC clamp meter in the gen input showed a current of only 0.4A when the inverter switched to charge mode.

The Excitation winding provides about 40v rms, but the reference voltage is taken from a tap on the main winding. I'm not sure of the exact position of the tap, or the ratio, but the AVR switches at about 17V input. (I have a spare AVR that has been reverse engineered....). Measuring the volts to ground from the Main winding, with the generator running at 235v, gave ~50V for N-G, and ~250V for L-G. Hence any capacitive load between either N-G or L-G (more significant) will produce current flowing in the ground fault to the rotor, and thence to the AVR. These capacitances are in emc filters, cables etc. and cannot be negated.